Reply
Highlighted
New member

Re: EMCP 4.2 Voltage

First confirm the type of avr on the model, be it R448 or VR6 u can alwaways use the voltage adjuster on the avr to reduce to what u want. Hope dis will be of help
Visitor

Re: EMCP 4.2 Voltage

You can adjust the voltage from configuration in your monitor without using ET, only from the menu>configuration of the control panel

Contributor

Re: EMCP 4.2 Voltage

MAIN MENU - CONTROL -  ADJUST SPEED and ADJUST VOLTAGE 

Press the scroll upkey in order to increase volt. and scroll down to decrease volt.

The volt can only be controlled from EMCP if  a CDVR is installed on the generator.

New member

EMCP 4.2 Voltage

Hi all,

 

I'm working on a 3406C generator with an EMCP 4.2 control unit. When I start the unit, the voltage is coming up to 220, which is way higher than I need it to be. I'm then having to bring it back down with the voltage adjust switch.  Is there a way to set the voltage to 210 in the EMCP somewhere without needing the CAT ET?  Thanks for your help everyone!