DVR Parameters

Hi

I am take the DVR 

P/N 155-3832

Please send the parameters setting 

please reply.

Visitor

Re: DVR Parameters

Hi arain1984

Below, there is a list of parameters with settings for DVR. It is the final setting in a customer. It is for 2 gensets in parallel. I'm not sure about the P/N because it is an old list.

 

DVR Parameters   –   906 KVA 

01 – Generator Output Voltage (V)	                480
02 – Ratio of Output Voltage to Sensing Voltage	2
03 – Generator Type	                                        4
04 – Rated Generator Output Current (A)	        2510
05 – CT Voltage At Rated Generator Current (V)	4,57
06 – Knee Frequency (Hz)	                                59,8
07 – Decreasing Volts/Hz Slope 1  (V/Hz)	        2,0
08 – Decreasing Volts/Hz Slope 2  (V/Hz)	        2,0
09 – Minimum Voltage (%)                           	60,0
10 – Underfrequency Point (Hz)	                        25,0
11 – Overvoltage Trip Point (%)	                        115
12 – Overvoltage Trip Time (s)	                        3
13 – Undervoltage Trip Point (%)	                        85
14 – Undervoltage Trip Time (s)	                        30
15 – Voltage Gain (IR Compensation) (%)	        0
16 – Integral Gain	                                        6,0
17 – Proportional Gain	                                        5,0
18 – Single Phase Sensing Select
0 = Three phase ; 1 = Single phase	                0
19 – Diode Monitor Trip Point	                        4,0
20 – Reverse VAR Trip Time	                                5,0
21 – Reverse VAR Fault Selection	                        1,0
22 – Droop/CCC Select (0 = Droop, 1 = CCC)	        0
30 – Droop Percentage (%)	                                5,0
31 – PF/KVAR Select (0 = PF, 1 = KVAR)	                0
32 – PF Reference	                                        0,82
33 – KVAR Reference	                                        1,0
34 – Reverse Power Trip Point (%)	                7,0
35 – Reverse Power Trip Time (s)	                        5,0
36 – Paralleling Integral Gain	                        -
37 – Paralleling Proportional Gain	                        -
38 – PF Switch Point (%)	                                -
50 – Generator Output Frequency (Hz)	
51 – Generator Output Voltage (V)	
52 – Generator Output Current (A)	
53 – Generator Reactive Output Current (A)	
54 – Generator Real Current (A)	
55 – Exciter Field Current (A)	
56 – Three Phase Kilowatts (“KE” and later) (kW)	
57 – Power Factor (PF)	
58 – Three Phase KVAR (“KE” and later)	
60 – Hours (h)	
70 – Voltage Adjust	
71 – PF/KVAR Adjust	
90 – Password	
91 – Software ID	
92 – Latest Fault	
93 – Previous Fault	
94 – Fault Clear	
95 – Alarm Fault	
96 – Shutdown Fault Reset	

 

Regards
E. Santos
Contributor

Re: DVR Parameters

this setting from Mr.Esantos for 60 HZ

Contributor

Re: DVR Parameters

Thanks for you

 

 


Contributor

Re: DVR Parameters

What meanes the code Appear the code 8888 on the DVR

And all DVR code send

New member

Re: DVR Parameters

P/N 883-59-000 recommend to you.iswisswatch

New member

Re: DVR Parameters

dear sir,

My generator previously use DVR model : 130-3475 and currently change to model 155-3835

is it suitable to use 630 KVA

if not  ok..can you provide the detail details of the setting

 

TQ