Re: Generator lockout

I think Tom makes a good point.  If it's got power going to the gen set, it needs to be turned off and locked off.  I think OHSA has some "fancy" wording for it, but that is their intent.

 

 

 

Larry Louree
Florida Registered Electrical Contractor
ER0013091
Apopka, Florida
New member Tom
New member

Re: Generator lockout

Lockout requirements depend on the type of service activity being performed on the gen set.  The typical minimum lockout points would include the following:

  1. Battery disconnect (to prevent engine from being started)
  2. Generator main breaker or downstream disconnect (although the gen set is usually connected to an ATS, the ATS can't be considered a LO point)

Depending on the configuration, the following additional lockout points might need to be considered:

  1. Heaters (likely to be fed from normal power source)
  2. control and or monitoring power (that control starting relay)

Hope this helps!

 

Contributor
Accepted Solution

Generator lockout

What's the best method to lock out a generator set for maintenance purposes?