Reply
Contributor

Re: Deep sea PLC Current Sensing Problem

Thanks alex644,
That engine is not with me now so I can not check.
And what if there is voltage between battery "-" and ground of engine?
What causes that voltage difference?
Contributor

Re: Deep sea PLC Current Sensing Problem

Yes i mean ground it's engine body, but sometimes there are a potention between earth and engine body. 1) check potentional between eng body and ground. Must be 0 volts.
2) check configuration soft: 3phase 4 wire. according picture. or you have another AC system?
Contributor

Re: Deep sea PLC Current Sensing Problem

What u mean by that Engine ground?
We normally connected battery "-" direct on the engine body, is that engine ground u mean to say?
Contributor

Re: Deep sea PLC Current Sensing Problem

Безымянный.png

check AC System: 3 Ph 4 wire

 

Contributor

Re: Deep sea PLC Current Sensing Problem

As i understand: you connected CT in star but disconnected 54-com from ground?
Num: 1, 15-19, 7 must have good ground. May be you have some voltage between "-" battery and engine ground?
I usually connect "-"bat and engine ground together - one point.
Contributor

Re: Deep sea PLC Current Sensing Problem

Which parameter we should check in configuration?
Contributor

Re: Deep sea PLC Current Sensing Problem

Hi,
Thanks alex644 for your reply.

Problem solved when we removed CT star point grounding.
But why ? ..I didn't get...

Any possible root cause from your side???
Contributor

Re: Deep sea PLC Current Sensing Problem

Check soft dse configuration.
Highlighted
Contributor

Deep sea PLC Current Sensing Problem

Hi Team,

 

We have Volvo penta TAD1641 engine in which we are using DSE8610.

 

Problem Description :

  1. When we are increasing load its current (Amps) readings not showing in Deep Sea controller.
  • we have checked Deep sea CT cables connection and also replaced but same problem
  • We have checked CTs and also for better replaced all, but same problem,
  • we have changed deep sea but same problem.
  • We have checked CT star point also, but not solved,

 

Can anyone help me out what could be the cause?