Reply
New member

Re: Reverse Power Fault NOT in Parallel

My colleague and I checked the wiring with another generator and it was the same. We're really scratching our heads with this one.
Contributor

Re: Reverse Power Fault NOT in Parallel

Hi 80

 

its posible the input to the contr system reading reverce because wire swap. CT measure direction wrong.

 

If wire connect worng reminal you get reverce power input.

 

New member

Reverse Power Fault NOT in Parallel

Good morning all. The generator in question is a MEP807A. When hooked up to the load bank, it runs fine, under 30kW. Once I put 30+kw on it, it will shutdown in approx. 7 seconds. The code on the GSC is SP2, DVR fault. The code on the DVR is 0705, reverse power shutdown. The gen is not in parallel so I'm confused as to why I would be getting this fault? My coworker and I have been troubleshooting for a couple weeks now and have come up empty. Thoughts?