Hi

I am take the DVR 

P/N 155-3832

Please send the parameters setting 

please reply.

Visitor

Re: DVR Parameters

Hi arain1984

Below, there is a list of parameters with settings for DVR. It is the final setting in a customer. It is for 2 gensets in parallel. I'm not sure about the P/N because it is an old list.

 

DVR Parameters   –   906 KVA 

01 – Generator Output Voltage (V)	                480
02 – Ratio of Output Voltage to Sensing Voltage	2
03 – Generator Type	                                        4
04 – Rated Generator Output Current (A)	        2510
05 – CT Voltage At Rated Generator Current (V)	4,57
06 – Knee Frequency (Hz)	                                59,8
07 – Decreasing Volts/Hz Slope 1  (V/Hz)	        2,0
08 – Decreasing Volts/Hz Slope 2  (V/Hz)	        2,0
09 – Minimum Voltage (%)                           	60,0
10 – Underfrequency Point (Hz)	                        25,0
11 – Overvoltage Trip Point (%)	                        115
12 – Overvoltage Trip Time (s)	                        3
13 – Undervoltage Trip Point (%)	                        85
14 – Undervoltage Trip Time (s)	                        30
15 – Voltage Gain (IR Compensation) (%)	        0
16 – Integral Gain	                                        6,0
17 – Proportional Gain	                                        5,0
18 – Single Phase Sensing Select
0 = Three phase ; 1 = Single phase	                0
19 – Diode Monitor Trip Point	                        4,0
20 – Reverse VAR Trip Time	                                5,0
21 – Reverse VAR Fault Selection	                        1,0
22 – Droop/CCC Select (0 = Droop, 1 = CCC)	        0
30 – Droop Percentage (%)	                                5,0
31 – PF/KVAR Select (0 = PF, 1 = KVAR)	                0
32 – PF Reference	                                        0,82
33 – KVAR Reference	                                        1,0
34 – Reverse Power Trip Point (%)	                7,0
35 – Reverse Power Trip Time (s)	                        5,0
36 – Paralleling Integral Gain	                        -
37 – Paralleling Proportional Gain	                        -
38 – PF Switch Point (%)	                                -
50 – Generator Output Frequency (Hz)	
51 – Generator Output Voltage (V)	
52 – Generator Output Current (A)	
53 – Generator Reactive Output Current (A)	
54 – Generator Real Current (A)	
55 – Exciter Field Current (A)	
56 – Three Phase Kilowatts (“KE” and later) (kW)	
57 – Power Factor (PF)	
58 – Three Phase KVAR (“KE” and later)	
60 – Hours (h)	
70 – Voltage Adjust	
71 – PF/KVAR Adjust	
90 – Password	
91 – Software ID	
92 – Latest Fault	
93 – Previous Fault	
94 – Fault Clear	
95 – Alarm Fault	
96 – Shutdown Fault Reset	

 

Regards
E. Santos
Contributor

Re: DVR Parameters

this setting from Mr.Esantos for 60 HZ

Contributor

Re: DVR Parameters

Thanks for you

 

 


Contributor

Re: DVR Parameters

What meanes the code Appear the code 8888 on the DVR

And all DVR code send

New member

Re: DVR Parameters

P/N 883-59-000 recommend to you.iswisswatch

New member

Re: DVR Parameters

dear sir,

My generator previously use DVR model : 130-3475 and currently change to model 155-3835

is it suitable to use 630 KVA

if not  ok..can you provide the detail details of the setting

 

TQ

New member

Re: DVR Parameters

We use the CAT P/n: 155-3832.

Please provide the parameters value settings.

 

Regards,

Pradeep

Highlighted
Super Contributor

Re: DVR Parameters

You will need to provide a lot more information if you want help on this.

 

Need to know what generator,

What is nominal voltage and frequency you operate at,

What kind of excitation system you have,

How you want the OEL setup done,

 