Re: 3508B - Air Shutoff Relay Open

RENR5004-03 Smiley Happy



View Laurentiu Iulian Iancu's profile on LinkedIn

Contributor

Re: 3508B - Air Shutoff Relay Open

Air shutoff  relay should be labled ASOS in the instrument panel.  By the way check you service records, as there was a modification to the older air shutoff solenoid circuits to make sure it was applied.
Visitor
Accepted Solution

3508B - Air Shutoff Relay Open

The alarm <Air Shutoff Relay Open> is released and disappears after <Reset> without any influences concerning the genset running condition. I'm wondering why the relay cannot be identified in my electrical drawings.

Could somebody give me a clue?

Many thanks in advance.  



View Laurentiu Iulian Iancu's profile on LinkedIn